Service entrance ? - from meter to panel

This topic can be found at:
https://sigforum.com/eve/forums/a/tpc/f/320601935/m/9640084324

April 29, 2017, 12:34 PM
Chris42
Service entrance ? - from meter to panel
OK, I am on site in southern WV, Appalachian Power Co.

Need to know cable size from the meter to the panel (about 9-10' total) for a 200A single phase, three wire connection.

Thanks,

from Chris in the middle of nowhere...
April 29, 2017, 12:43 PM
Rustyblade
do you need an answer to check up on work someone else did?


Do not necessarily attribute someone's nasty or inappropriate actions as intended when it may be explained by ignorance or stupidity.
April 29, 2017, 01:00 PM
Chris42
No, doing upgrade to old. Need wire gage size. Two hots and a neutral.
April 29, 2017, 01:17 PM
sandman76
4/0 AL or 2/0 CU for residential. 250MCM AL or 3/0 CU for commercial.