OK, I am on site in southern WV, Appalachian Power Co. Need to know cable size from the meter to the panel (about 9-10' total) for a 200A single phase, three wire connection. Thanks, from Chris in the middle of nowhere... | ||
|
I will get by |
do you need an answer to check up on work someone else did? Do not necessarily attribute someone's nasty or inappropriate actions as intended when it may be explained by ignorance or stupidity. | |||
|
Member |
No, doing upgrade to old. Need wire gage size. Two hots and a neutral. | |||
|
Common sense is genius dressed in its working clothes |
4/0 AL or 2/0 CU for residential. 250MCM AL or 3/0 CU for commercial. _______________________ “There is more stupidity than hydrogen in the universe, and it has a longer shelf life.” ― Frank Zappa | |||
|