Anybody Familiar With Tilt Up Construction - Engineering Question Login/Join 
safe & sound
Picture of a1abdj
posted
Our new school has a small gymnasium built as a storm shelter. Concrete tilt up construction. Each panel has two embedded steel pieces on each side which split the panel into thirds. A roughly 12" square plate is welded overlapping two panels at each of these locations.

Are these plates only to hold the walls together until the roof is installed, or do they play a role in the structure itself, and/or its ability to withstand a tornado?

The reason I ask is that it looked like a first grader did the welding, and the panels are often not aligned flat where shimming was performed (poorly) to get the welded plate to sit across both panels.


________________________



www.zykansafe.com
 
Posts: 16276 | Location: St. Charles, MO, USA | Registered: September 22, 2003Reply With QuoteReport This Post
Observer
Picture of phxtoad
posted Hide Post
I am familiar with tilt, but as an Architect - not a Structural Engineer. I think it’s a little of both: They get welded on prior to roof install for alignment and to limit movement mostly - thus the ‘quick’ welds. Once the roof diaphragm is complete, that takes the lateral load. Each panel technically spans from floor to roof. During erection, the panels are braced, but if a brace anchor fails, then the ‘tabs’ keep things together - transferring load to the adjacent panels.


phxtoad

"Careful man, there's a beverage here!"
 
Posts: 448 | Location: Tempe, Arizona | Registered: October 01, 2013Reply With QuoteReport This Post
semi-reformed sailor
Picture of MikeinNC
posted Hide Post
Just watched this, looks like they are just for the bracing part. I guess putting the roof on locks it all into place

https://www.youtube.com/watch?v=kC_pEaccZQA




“You may beat me, but you will never win.” sigmonkey-2020

“ in my opinion, anything that we can do to trigger a potential aneurysm in a leftist is a good thing and worth doing” nhtagmember 2025
 
Posts: 12309 | Location: Temple, Texas! | Registered: October 07, 2006Reply With QuoteReport This Post
safe & sound
Picture of a1abdj
posted Hide Post
Adding photos of the plates in question:







________________________



www.zykansafe.com
 
Posts: 16276 | Location: St. Charles, MO, USA | Registered: September 22, 2003Reply With QuoteReport This Post
Donate Blood,
Save a Life!
Picture of StarTraveler
posted Hide Post
The plates and welds vary depending on the design of the panels. If they’re used as individual wall panels with another lateral system or as shear walls for in-plane wind or seismic forces (I.e., parallel to the wall length) those maybe good enough. Occasionally several panels may need to be linked together to make them act as a combined shear wall. In such cases, there are typically more embeds and plates and welding is more extensive.

Most jurisdictions following the International Building Code now require a Special Inspector to look at welds to make sure they meet project requirements. That’s the question I’d ask to see if inspections are being done and, if so, do they meet the requirements. If there aren’t any inspections being performed, the question might be “why not?”


***

"Aut viam inveniam aut faciam (I will either find a way or make one)." -- Hannibal Barca
 
Posts: 2326 | Location: Georgia | Registered: July 19, 2008Reply With QuoteReport This Post
Member
Picture of JoseyWales2
posted Hide Post
If they were meant to be structural welds, I would think it would be a continuous weld, not a spot weld. And there seems to be a tremendous variation in that welded plate thickness.

I think StarTraveler has a good idea, ask if inspections are being done and what requirements need to be met to meet code.


----------------------------------
"These things you say we will have, we already have."
"That's true. I ain't promising you nothing extra."
 
Posts: 680 | Location: Missouri | Registered: October 17, 2010Reply With QuoteReport This Post
Donate Blood,
Save a Life!
Picture of StarTraveler
posted Hide Post
quote:
Originally posted by JoseyWales2:
If they were meant to be structural welds, I would think it would be a continuous weld, not a spot weld. And there seems to be a tremendous variation in that welded plate thickness.


Not necessarily on the continuous versus intermittent welds; structural engineers frequently specify intermittent welds if they will carry the required load since welding is expensive. However, I agree on the variation, though part of that appears to be due to the shims required, probably due to the embeds being off a little (or a lot?).


***

"Aut viam inveniam aut faciam (I will either find a way or make one)." -- Hannibal Barca
 
Posts: 2326 | Location: Georgia | Registered: July 19, 2008Reply With QuoteReport This Post