SIGforum.com    Main Page  Hop To Forum Categories  The Lounge    Why would a dozen or more electric circuits stop working?
Page 1 2 3 4 
Go
New
Find
Notify
Tools
Reply
  
Why would a dozen or more electric circuits stop working? Login/Join 
Savor the limelight
posted
My Dad called me last night and said a dozen or more circuits in his house suddenly stopped working. Lights and outlets in various rooms, the AC, etc. He says the breakers are all on. He also says the non-working circuits are on both sides of the panels and some of the lights will come on for a few seconds every once in awhile even though the switches are off.
 
Posts: 11991 | Location: SWFL | Registered: October 10, 2007Reply With QuoteReport This Post
Member
posted Hide Post
Might be some type of grounding issue? Just a guess.


End of Earth: 2 Miles
Upper Peninsula: 4 Miles
 
Posts: 16554 | Location: Marquette MI | Registered: July 08, 2014Reply With QuoteReport This Post
Member
posted Hide Post
Trapper - Have your dad look for a tripped GFI plug in his bathrooms, kitchen area, or outside plug units. I bet he has a tripped GFI that is actually the first plug on a series of plugs.
 
Posts: 3460 | Location: MS | Registered: December 16, 2004Reply With QuoteReport This Post
Green grass and
high tides
Picture of old rugged cross
posted Hide Post
something like one leg of his power is not copacetic for some reason maybe.
Rodent chewed wires?



"Practice like you want to play in the game"
 
Posts: 19950 | Registered: September 21, 2005Reply With QuoteReport This Post
Member
posted Hide Post
I believe things like that are possible when you lose a leg of power coming in from the utility. He can report it to the power company or have an electrician check incoming voltage at the meter.
 
Posts: 831 | Registered: February 07, 2004Reply With QuoteReport This Post
Vote the
BASTIDS OUT!
Picture of yanici
posted Hide Post
quote:
Originally posted by old rugged cross:
something like one leg of his power is not copacetic for some reason maybe.
Rodent chewed wires?


That is probably correct. Looks like he lost one hot leg in the panel. Could be a bad main breaker or even in the meter socket, or a problem with the line coming into the house. Be nice if he knows how to check for incoming power on the wires that feed into his main breaker.


John

"Building a wall will violate the rights of millions of illegals." [Nancy Pelosi]
 
Posts: 2440 | Location: N.E. Massachusetts | Registered: June 05, 2009Reply With QuoteReport This Post
Savor the limelight
posted Hide Post
Shoot, I didn’t even think of the incoming feed. Thanks guys, I’ll bet that’s it. Just had a new house built next door and hooked to the same transformer my dad’s house is on. Plus with the hurricane, there may well be an issue with the transformer.
 
Posts: 11991 | Location: SWFL | Registered: October 10, 2007Reply With QuoteReport This Post
Optimistic Cynic
Picture of architect
posted Hide Post
I would hope that a genuine electrician will chime in, Skins, Skins, wherefore art thou Skins? But, this sounds like a potentially dangerous situation to me, an intermittent connection with the energy levels found in residential electrical circuitry can easily cause excessive heat buildup leading to a fire. I would speculate that this is a grounding issue where a neutral connection has worked loose, or built up corrosion in a connector possibly leading to a high resistance partial connection. High resistance == heat. If the lights come on when the switch is off, their must be a current flow, perhaps the grounding circuit has been energized.

This is not something to put off, get a licensed electrician on it right away. At the very least, I would de-energize the circuit(s) at the breaker panel, pull all outlet and switch cover plates and closely examine all connections and conductors for corrosion and signs of arcing. A multimeter would help here. The intermittent could be inside a switch or outlet (e.g. a GFI pass-through outlet) so don't rely on a visual inspection as determinant. And, if you find a problem, do not assume it is the only one. Electrical problems can propagate, e.g. where heat buildup causes insulation failure in an adjacent circuit.
 
Posts: 6934 | Location: NoVA | Registered: July 22, 2009Reply With QuoteReport This Post
Nullus Anxietas
Picture of ensigmatic
posted Hide Post
quote:
Originally posted by old rugged cross:
something like one leg of his power is not copacetic for some reason maybe.
That was my first thought, until I read...
quote:
Originally posted by trapper189:
He also says the non-working circuits are on both sides of the panels ...
So that kind of rules that out, in my mind.


Then there's...
quote:
Originally posted by trapper189:
... and some of the lights will come on for a few seconds every once in awhile even though the switches are off.
Poltergeists?

Seriously: That literally does not make any sense at all. If they're actually old school switches: Off is off. The hot side of the circuit is open. Current literally cannot flow.

Unless Joe Homeowner has done some truly strange things with the house wiring, the likes of which I cannot imagine could result in such a thing--and I've been doing electricity for nigh on sixty years.

But, ICBW. Hopefully Skins will be along shortly with an possible explanation.
quote:
Originally posted by architect:
I would hope that a genuine electrician will chime in, Skins, Skins, wherefore art thou Skins? But, this sounds like a potentially dangerous situation to me, ...
It sure does!

Personally, I'd be inclined to go out to the distribution panel(s) and throw the main disconnects on each.

trapper189, does your dad have LED lighting, by chance?



"America is at that awkward stage. It's too late to work within the system,,,, but too early to shoot the bastards." -- Claire Wolfe
"If we let things terrify us, life will not be worth living." -- Seneca the Younger, Roman Stoic philosopher
 
Posts: 26031 | Location: S.E. Michigan | Registered: January 06, 2008Reply With QuoteReport This Post
My other Sig
is a Steyr.
Picture of .38supersig
posted Hide Post
Missing three phase power?

Are all the dead circuits on the same side of the breaker box plus the dryer & range?



 
Posts: 9530 | Location: Somewhere looking for ammo that nobody has at a place I haven't been to for a pistol I couldn't live without... | Registered: December 02, 2014Reply With QuoteReport This Post
semi-reformed sailor
Picture of MikeinNC
posted Hide Post
Lightning is my guess



"Violence, naked force, has settled more issues in history than has any other factor.” Robert A. Heinlein

“You may beat me, but you will never win.” sigmonkey-2020

“A single round of buckshot to the torso almost always results in an immediate change of behavior.” Chris Baker
 
Posts: 11568 | Location: Temple, Texas! | Registered: October 07, 2006Reply With QuoteReport This Post
Member
posted Hide Post
Acrylic, acrylic, acrylic !
 
Posts: 1036 | Location: Central Ohio | Registered: January 05, 2018Reply With QuoteReport This Post
אַרְיֵה
Picture of V-Tail
posted Hide Post
quote:
Originally posted by .38supersig:

Are all the dead circuits on the same side of the breaker box
quote:
From the Original Post:

the non-working circuits are on both sides of the panels



הרחפת שלי מלאה בצלופחים
 
Posts: 31699 | Location: Central Florida, Orlando area | Registered: January 03, 2010Reply With QuoteReport This Post
Member
posted Hide Post
quote:
Originally posted by ensigmatic:
quote:
Originally posted by old rugged cross:
something like one leg of his power is not copacetic for some reason maybe.
That was my first thought, until I read...
quote:
Originally posted by trapper189:
He also says the non-working circuits are on both sides of the panels ...
So that kind of rules that out, in my mind.


Then there's...
quote:
Originally posted by trapper189:
... and some of the lights will come on for a few seconds every once in awhile even though the switches are off.
Poltergeists?

Seriously: That literally does not make any sense at all. If they're actually old school switches: Off is off. The hot side of the circuit is open. Current literally cannot flow.

Unless Joe Homeowner has done some truly strange things with the house wiring, the likes of which I cannot imagine could result in such a thing--and I've been doing electricity for nigh on sixty years.

But, ICBW. Hopefully Skins will be along shortly with an possible explanation.
quote:
Originally posted by architect:
I would hope that a genuine electrician will chime in, Skins, Skins, wherefore art thou Skins? But, this sounds like a potentially dangerous situation to me, ...
It sure does!

Personally, I'd be inclined to go out to the distribution panel(s) and throw the main disconnects on each.

trapper189, does your dad have LED lighting, by chance?


Both sides of a panel have both legs. Every other spot is on a different leg. That is how a 220 breaker works.
 
Posts: 1104 | Location: New Jersey | Registered: August 16, 2009Reply With QuoteReport This Post
Unflappable Enginerd
Picture of stoic-one
posted Hide Post
quote:
Originally posted by .38supersig:
Missing three phase power?

Are all the dead circuits on the same side of the breaker box plus the dryer & range?
Can't say I've spent much time in any "home" on this planet with 3 phase power... Razz


__________________________________

NRA Benefactor
I lost all my weapons in a boating, umm, accident.
http://www.aufamily.com/forums/
 
Posts: 6400 | Location: Headland, AL | Registered: April 19, 2006Reply With QuoteReport This Post
Member
posted Hide Post
I have seen this exact same issue . One side of the main breaker is possibly bad . That " leg " of the circuit feeds breakers on both sides of the panel .
One leg of the 240v input is open somewhere .
 
Posts: 4422 | Location: Down in Louisiana . | Registered: February 27, 2009Reply With QuoteReport This Post
Nullus Anxietas
Picture of ensigmatic
posted Hide Post
quote:
Originally posted by PeteF:
Both sides of a panel have both legs. Every other spot is on a different leg. That is how a 220 breaker works.
Oops! You're right. Synapse lapse on my part.



"America is at that awkward stage. It's too late to work within the system,,,, but too early to shoot the bastards." -- Claire Wolfe
"If we let things terrify us, life will not be worth living." -- Seneca the Younger, Roman Stoic philosopher
 
Posts: 26031 | Location: S.E. Michigan | Registered: January 06, 2008Reply With QuoteReport This Post
Savor the limelight
posted Hide Post
Both feeds into the panel measure 120v. He's got an electrician coming tomorrow and all the breakers except the fridge are off until then. He'll stay in the addition, which has its own electrical panel and AC, where everything seems to be working.

He does not have LEDs. Maybe it's the main breaker in the panel, but he's reached his limit on troubleshooting at this point. There's a surge protector wired into the panel in question, but I don't know if that could be the issue.
 
Posts: 11991 | Location: SWFL | Registered: October 10, 2007Reply With QuoteReport This Post
Member
posted Hide Post
quote:
Originally posted by trapper189:
Both feeds into the panel measure 120v. He's got an electrician coming tomorrow and all the breakers except the fridge are off until then. He'll stay in the addition, which has its own electrical panel and AC, where everything seems to be working.

He does not have LEDs. Maybe it's the main breaker in the panel, but he's reached his limit on troubleshooting at this point. There's a surge protector wired into the panel in question, but I don't know if that could be the issue.
Both legs will read 120 volts with one leg out . You're reading the same leg that's feeding through a device . Water heater element would be my guess . You learn things like this over the years .
 
Posts: 4422 | Location: Down in Louisiana . | Registered: February 27, 2009Reply With QuoteReport This Post
Member
posted Hide Post
A few years back we had an outlet that was behind our bed. The wife pushed the bed tight against the wall which cracked the outlet. All outlets and lights down the line started working sporadically. That would explain one circuit but not the problem your dad is having. Is the panel OK. That is the only thing I can think of that would be common to all problematic circuits.
 
Posts: 7781 | Registered: October 31, 2008Reply With QuoteReport This Post
  Powered by Social Strata Page 1 2 3 4  
 

SIGforum.com    Main Page  Hop To Forum Categories  The Lounge    Why would a dozen or more electric circuits stop working?

© SIGforum 2024