Trying to trouble shot a house ac.
Air will blow but outside unit is not turning
The circuit board is flashing a code. 8 fast. 3 slow
Board is. HK38EA004
Can’t find trouble codes for this board.
July 08, 2019, 07:37 PM
Skins2881Look on backside of the door you removed to access the board, should be printed there or on the side of furnace enclosure. Or check owners manual.
July 08, 2019, 07:59 PM
comet24No codes just a wiring diagram
July 08, 2019, 08:00 PM
PowerSurgeLooks like low pressure lockout:
https://dms.hvacpartners.com/d...ec%26CurrentPage%3D1If the system pressure is too low, the compressor won’t run so as to protect itself.
July 08, 2019, 09:41 PM
comet24quote:
Originally posted by PowerSurge:
Looks like low pressure lockout:
https://dms.hvacpartners.com/d...ec%26CurrentPage%3D1If the system pressure is too low, the compressor won’t run so as to protect itself.
Thank you.
So this thing has a Carrier Infinity Thermostat.
Got it to show the fualt what was the same as PowerSurge listed. The thermostat said timed out for 4 hours. When I saw this we had about 15 minutes till it would time back. It did come back on and is working normally.
Not sure what caused the issue.
This wasn't my house. This was a good friends house who has 3 young kids, I was trying to help out since no one was coming out tonight to look at it.
July 08, 2019, 10:39 PM
Excam_ManWhile operating the LPS opens and shuts off the unit. Pressures equalize, closing safety switch and the unit is up and running again after timeout.
Could be any one of several possibilities:
Dirty filter/s
Dirty evaporator coil
Dirty squirrel cage
Weak blower motor
Blocked/closed registers
Refrigerant restriction
Low refrigerant
If new install,
Inadequate supply/return ducting
Improper blower speed (CFM)