Trying to trouble shot a house ac.

Air will blow but outside unit is not turning

The circuit board is flashing a code. 8 fast. 3 slow

Board is. HK38EA004

Can’t find trouble codes for this board.


_____________________________________

Because in the end, you won’t remember the time you spent working in the office or mowing your lawn. Climb that goddamn mountain. Jack Kerouac
 
Posts: 16483 | Registered: March 27, 2004Reply With QuoteReport This Post
Ammoholic
Picture of Skins2881
posted Hide Post
Look on backside of the door you removed to access the board, should be printed there or on the side of furnace enclosure. Or check owners manual.



Jesse

Sic Semper Tyrannis
 
Posts: 21336 | Location: Loudoun County, Virginia | Registered: December 27, 2014Reply With QuoteReport This Post
Just for the
hell of it
Picture of comet24
posted Hide Post
No codes just a wiring diagram


_____________________________________

Because in the end, you won’t remember the time you spent working in the office or mowing your lawn. Climb that goddamn mountain. Jack Kerouac
 
Posts: 16483 | Registered: March 27, 2004Reply With QuoteReport This Post
Member
Picture of PowerSurge
posted Hide Post
Looks like low pressure lockout: https://dms.hvacpartners.com/d...ec%26CurrentPage%3D1

If the system pressure is too low, the compressor won’t run so as to protect itself.


———————————————
The fool hath said in his heart, There is no God. Psalm 14:1
 
Posts: 4047 | Location: Northeast Georgia | Registered: November 18, 2017Reply With QuoteReport This Post
Member
posted Hide Post
^^^ Ding ding ding. Smile




 
Posts: 10062 | Registered: October 15, 2008Reply With QuoteReport This Post
Just for the
hell of it
Picture of comet24
posted Hide Post
quote:
Originally posted by PowerSurge:
Looks like low pressure lockout: https://dms.hvacpartners.com/d...ec%26CurrentPage%3D1

If the system pressure is too low, the compressor won’t run so as to protect itself.


Thank you.

So this thing has a Carrier Infinity Thermostat.

Got it to show the fualt what was the same as PowerSurge listed. The thermostat said timed out for 4 hours. When I saw this we had about 15 minutes till it would time back. It did come back on and is working normally.

Not sure what caused the issue.

This wasn't my house. This was a good friends house who has 3 young kids, I was trying to help out since no one was coming out tonight to look at it.


_____________________________________

Because in the end, you won’t remember the time you spent working in the office or mowing your lawn. Climb that goddamn mountain. Jack Kerouac
 
Posts: 16483 | Registered: March 27, 2004Reply With QuoteReport This Post
Member
posted Hide Post
While operating the LPS opens and shuts off the unit. Pressures equalize, closing safety switch and the unit is up and running again after timeout.

Could be any one of several possibilities:
Dirty filter/s
Dirty evaporator coil
Dirty squirrel cage
Weak blower motor
Blocked/closed registers
Refrigerant restriction
Low refrigerant

If new install,
Inadequate supply/return ducting
Improper blower speed (CFM)




 
Posts: 10062 | Registered: October 15, 2008Reply With QuoteReport This Post