Trying to trouble shot a house ac. Air will blow but outside unit is not turning The circuit board is flashing a code. 8 fast. 3 slow Board is. HK38EA004 Can’t find trouble codes for this board. _____________________________________ Because in the end, you won’t remember the time you spent working in the office or mowing your lawn. Climb that goddamn mountain. Jack Kerouac | ||
|
Ammoholic |
Look on backside of the door you removed to access the board, should be printed there or on the side of furnace enclosure. Or check owners manual. Jesse Sic Semper Tyrannis | |||
|
Just for the hell of it |
No codes just a wiring diagram _____________________________________ Because in the end, you won’t remember the time you spent working in the office or mowing your lawn. Climb that goddamn mountain. Jack Kerouac | |||
|
Member |
Looks like low pressure lockout: https://dms.hvacpartners.com/d...ec%26CurrentPage%3D1 If the system pressure is too low, the compressor won’t run so as to protect itself. ——————————————— The fool hath said in his heart, There is no God. Psalm 14:1 | |||
|
Member |
^^^ Ding ding ding. | |||
|
Just for the hell of it |
Thank you. So this thing has a Carrier Infinity Thermostat. Got it to show the fualt what was the same as PowerSurge listed. The thermostat said timed out for 4 hours. When I saw this we had about 15 minutes till it would time back. It did come back on and is working normally. Not sure what caused the issue. This wasn't my house. This was a good friends house who has 3 young kids, I was trying to help out since no one was coming out tonight to look at it. _____________________________________ Because in the end, you won’t remember the time you spent working in the office or mowing your lawn. Climb that goddamn mountain. Jack Kerouac | |||
|
Member |
While operating the LPS opens and shuts off the unit. Pressures equalize, closing safety switch and the unit is up and running again after timeout. Could be any one of several possibilities: Dirty filter/s Dirty evaporator coil Dirty squirrel cage Weak blower motor Blocked/closed registers Refrigerant restriction Low refrigerant If new install, Inadequate supply/return ducting Improper blower speed (CFM) | |||
|