HVAC Question Login/Join 
אַרְיֵה
Picture of V-Tail
posted
We have at least one HVAC professional here on SIGforum; I have a question for him / them:

A lightning strike in the back yard caused a major power surge in our house. Damage included the HVAC air handler, shorting one of the conductors in the cable bundle between the air handler and the thermostat. Fried the thermostat, which has been replaced, and there was a spare wire in the cable bundle, so the wiring is now functional.

There is a refrigerant leak in the air handler. A replacement has been ordered and should arrive in a few days. Meantime, "Air Conditioning Joe" has been replenishing the refrigerant on a daily basis to give us some relief in these 90° Florida days.

Here's my question: "Air Conditioning Joe" told us to keep the thermostat set to a low temperature, stating that by keeping the system running, the refrigerant leak will be minimized. Google tells me the opposite. What is the correct answer?



הרחפת שלי מלאה בצלופחים
 
Posts: 33698 | Location: Central Florida, Orlando area | Registered: January 03, 2010Reply With QuoteReport This Post
Technically Adaptive
posted Hide Post
From an automotive perspective. The air handler (evaporator) has a lower pressure when running than it does when shut off. Pressure equalizes when static, so, I would keep it running.
 
Posts: 1980 | Location: Willcox, AZ | Registered: September 24, 2006Reply With QuoteReport This Post
Ammoholic
Picture of Skins2881
posted Hide Post
quote:
Originally posted by rizzle:
From an automotive perspective. The air handler (evaporator) has a lower pressure when running than it does when shut off. Pressure equalizes when static, so, I would keep it running.


Unless high side leak or enough leak happens. Did they state it's an evap coil leak or low side leak?



Jesse

Sic Semper Tyrannis
 
Posts: 21824 | Location: Loudoun County, Virginia | Registered: December 27, 2014Reply With QuoteReport This Post
Member
posted Hide Post
What rizzle said, but not only are you losing freon but you are also losing the oil that lubricates the compressor, so there is a risk of locking up the compressor if it's leaking so much he has to charge it daily.

That being said, if you have a lightning strike, almost everything in your house with a circuit board will fail within the next year, even if it is currently working now. So I would have insurance cover all of those items from tv's to microwave to clock radio.
 
Posts: 21799 | Registered: June 12, 2005Reply With QuoteReport This Post
Technically Adaptive
posted Hide Post
quote:
Originally posted by Skins2881:
quote:
Originally posted by rizzle:
From an automotive perspective. The air handler (evaporator) has a lower pressure when running than it does when shut off. Pressure equalizes when static, so, I would keep it running.


Unless high side leak or enough leak happens. Did they state it's an evap coil leak or low side leak?


I don't know where the A/c leak is, but if it is on the low side, keep it running, Considering the guy doing the work knows where the leak is, that would be his reason to keep it running.
 
Posts: 1980 | Location: Willcox, AZ | Registered: September 24, 2006Reply With QuoteReport This Post
Member
Picture of 4MUL8R
posted Hide Post
Did you ask google the obvious follow up question?

Why then does my technician instruct me to run it as much as possible?

Google has the answer.


-------
Trying to simplify my life...
 
Posts: 6247 | Location: Commonwealth of Virginia | Registered: January 15, 2007Reply With QuoteReport This Post