You've already got the answer. No.

If it was me, I'd measure the run, if it's under 250' buy a roll of 10-2 UF. Then add 20a rated male/female ends

This is still way undersized for 3% VD, but most equipment will run down to 110v. If it's purely resistive heat then you will just get lower heat output the lower voltage goes. I = V/R. The lower the V, the lower the I.



Jesse

Sic Semper Tyrannis
 
Posts: 21358 | Location: Loudoun County, Virginia | Registered: December 27, 2014Reply With QuoteReport This Post
Member
posted Hide Post
quote:
Originally posted by Sig Vicious:
300 feet is a long run and will cause a voltage drop at your load (heater). When voltage goes down, current goes up. The resistive load of the heater is less affected by this than an inductive (motor) load.

Using #14 cable gives a voltage drop of 20 volts. This could work for a resistive load but, as pointed out above, you will not get as much heating from it an the current will rise .


For a resistive heater load some of the info above is incorrect. I = E/R which means the current is determined by the voltage divided by the resistance. If the heater is a pure resistance (R), its value doesn’t change no matter what voltage is applied to it (as long as you’re not melting its wires or causing other physical damage). If the long extension cord (also acting like a low value resistor) causes the voltage (E) at the heater to be 20% less than it should be, then the current will also be 20% less (not more) than it should have been if there were no voltage drop. It’s ok to run the heater at the lower voltage value as long as the 20% lower amount of heat doesn’t cause a problem (insufficient heat to melt ice so the cows can get a drink, etc).
 
Posts: 1248 | Location: NE Indiana  | Registered: January 20, 2011Reply With QuoteReport This Post
To all of you who are serving or have served our country, Thank You
Picture of Jelly
posted Hide Post
Answer is No.

How big of stock tank are we talking about? How cold are we talking about. Sure a 500 W would not due?
 
Posts: 2681 | Registered: March 15, 2004Reply With QuoteReport This Post
Member
Picture of 4MUL8R
posted Hide Post
I like Jelly's suggestion. 500W would be a low cost temporary fix, and surely would keep the tank water from freezing. Less risk, less cost for the extension cord, and a safe alternative.


-------
Trying to simplify my life...
 
Posts: 5316 | Location: Commonwealth of Virginia | Registered: January 15, 2007Reply With QuoteReport This Post
Peace through
superior firepower
Picture of parabellum
posted Hide Post
I guess we do have extension cord experts here.
 
Posts: 110258 | Registered: January 20, 2000Reply With QuoteReport This Post
Member
posted Hide Post
Looks like the standard grade orange 12ga extension cords are the cheapest option. Three in series is about as far as I would use for 1500w.
Using 12/3 romex cable and installing plug ends on it would probably cost a little more but you get an honest 12ga wire. It also looks like 10/3 extension cords or romex more than doubles the cost.
I would decide which option will leave you the most useful leftovers when you get the issue fixed.


“That’s what.” - She
 
Posts: 429 | Location: Kentucky | Registered: June 06, 2021Reply With QuoteReport This Post
Member
Picture of Blume9mm
posted Hide Post
I would for sure go with 12/3... but if it is temporary... why not just use Romex wire.

Now with that said, from my experience you are going to get a serious voltage drop... I suspect you'll be down to around 105 volts... this won't be a problem if the heater is just some basic resistive device with no solid state fancy new age stuff added.... other than a thermostat....


My Native American Name:
"Runs with Scissors"
 
Posts: 4441 | Location: Greenville, SC | Registered: January 30, 2017Reply With QuoteReport This Post
Cold Ass Honkey
Picture of Sig Vicious
posted Hide Post
quote:
Originally posted by tsmccull:
quote:
Originally posted by Sig Vicious:
300 feet is a long run and will cause a voltage drop at your load (heater). When voltage goes down, current goes up. The resistive load of the heater is less affected by this than an inductive (motor) load.

Using #14 cable gives a voltage drop of 20 volts. This could work for a resistive load but, as pointed out above, you will not get as much heating from it an the current will rise .


For a resistive heater load some of the info above is incorrect. I = E/R which means the current is determined by the voltage divided by the resistance. If the heater is a pure resistance (R), its value doesn’t change no matter what voltage is applied to it (as long as you’re not melting its wires or causing other physical damage). If the long extension cord (also acting like a low value resistor) causes the voltage (E) at the heater to be 20% less than it should be, then the current will also be 20% less (not more) than it should have been if there were no voltage drop. It’s ok to run the heater at the lower voltage value as long as the 20% lower amount of heat doesn’t cause a problem (insufficient heat to melt ice so the cows can get a drink, etc).


You are correct.
I even though I knew that the load is resistive, I treated as though it were an inductive load.
I have edited my post to cause less confusion.


------------------------------
Never fully gruntled.
 
Posts: 2181 | Location: OR-ee-GUN | Registered: December 18, 2005Reply With QuoteReport This Post
Lawyers, Guns
and Money
Picture of chellim1
posted Hide Post
quote:
Originally posted by parabellum:
I guess we do have extension cord experts here.

Definitely not me...
I tried running 4 sets of c9 Christmas lights through a dinky little extension cord and blew it out. With a heavier gauge extension cord I was able to get it all working, but I have no knowledge of the specifics.



"Some things are apparent. Where government moves in, community retreats, civil society disintegrates and our ability to control our own destiny atrophies. The result is: families under siege; war in the streets; unapologetic expropriation of property; the precipitous decline of the rule of law; the rapid rise of corruption; the loss of civility and the triumph of deceit. The result is a debased, debauched culture which finds moral depravity entertaining and virtue contemptible."
-- Justice Janice Rogers Brown

"The United States government is the largest criminal enterprise on earth."
-rduckwor
 
Posts: 24960 | Location: St. Louis, MO | Registered: April 03, 2009Reply With QuoteReport This Post