Help - it's almost 90 degrees inside the house! Login/Join 
Member
Picture of konata88
posted
It's hot outside.

Inside the temp is approaching 90 degrees. I need some help troubleshooting the AC.

The thermostat seems to be working. And it triggers the fan to come on. The problem is the unit outside (condenser?) isn't coming on. I can hear some electrical humming but the pump or blower fan aren't on (I need to double check the blower fan but definitely the loud condenser isn't on).

I replaced the caps at the condenser and upstairs (at the furnace / blower / evaporator) about 5-7 years ago. The one outside seems okay - at least nothing visually wrong. Haven't checked upstairs yet.

I'm thinking something at the condenser unit is broken? But there doesn't seem to be much there except the cap and some sort of copper coil (small transformer?).

I'd appreciate some help trying to figure out what might be wrong and how to test. Then perhaps to find a replacement part.




"Wrong does not cease to be wrong because the majority share in it." L.Tolstoy
"A government is just a body of people, usually, notably, ungoverned." Shepherd Book
 
Posts: 13069 | Location: In the gilded cage | Registered: December 09, 2007Reply With QuoteReport This Post
Technically Adaptive
posted Hide Post
If the (loud) fan on the outside unit is not coming on, and it's humming, I would be thinking capacitor. Don't let sit and and try to start for too long.
 
Posts: 1358 | Location: Willcox, AZ | Registered: September 24, 2006Reply With QuoteReport This Post
Page late and a dollar short
posted Hide Post
Start/run capacitor is my bet. Last one that I had fail didn’t swell up or show any outward signs of failure.


-------------------------------------——————
————————--Ignorance is a powerful tool if applied at the right time, even, usually, surpassing knowledge(E.J.Potter, A.K.A. The Michigan Madman)
 
Posts: 8350 | Location: Livingston County Michigan USA | Registered: August 11, 2002Reply With QuoteReport This Post
Member
Picture of konata88
posted Hide Post
Thanks guys. Is this a premature failure or is 5-7 years a reasonable lifespan? Just wondering if I should buy 2 (and replace the one in the attic as well) or just replace the one.

Is there a way to test this without killing myself? I have a Fluke.




"Wrong does not cease to be wrong because the majority share in it." L.Tolstoy
"A government is just a body of people, usually, notably, ungoverned." Shepherd Book
 
Posts: 13069 | Location: In the gilded cage | Registered: December 09, 2007Reply With QuoteReport This Post
Itchy was taken
Picture of scratchy
posted Hide Post
My AC had the same symptoms. It was the start/run cap. In my case, it is a 5/45 ufd Capacitor, costs around $25


_________________
This space left intentionally blank.
 
Posts: 4093 | Location: Colorado | Registered: August 24, 2008Reply With QuoteReport This Post
Age Quod Agis
Picture of ArtieS
posted Hide Post
Almost certainly the capacitor.

Be careful, though. A short discharge through one can be dangerous.



"I vowed to myself to fight against evil more completely and more wholeheartedly than I ever did before. . . . That’s the only way to pay back part of that vast debt, to live up to and try to fulfill that tremendous obligation."

Alfred Hornik, Sunday, December 2, 1945 to his family, on his continuing duty to others for surviving WW II.
 
Posts: 12910 | Location: Central Florida | Registered: November 02, 2008Reply With QuoteReport This Post
Fighting the good fight
Picture of RogueJSK
posted Hide Post
quote:
Originally posted by konata88:
Thanks guys. Is this a premature failure or is 5-7 years a reasonable lifespan?


~5 years is the average lifespan, and often less. Based on that age and the symptoms (thermostat and fan work, but compressor and/or blower won't kick on), it's most likely going to be that start/run capacitor on your outside unit.

quote:
Is there a way to test this without killing myself? I have a Fluke.


Yes, if you have a multimeter. It's pretty simple. There are step by step Youtube tutorials for testing a HVAC capacitor, such as: https://www.youtube.com/watch?v=m2wHS4uJUfU

But even if you don't want to mess with testing it or don't have access to a multimeter, just tossing a new $20 capacitor on the outside unit would be a reasonable first troubleshooting step in this case.
 
Posts: 32992 | Location: Northwest Arkansas | Registered: January 06, 2008Reply With QuoteReport This Post
Thank you
Very little
Picture of HRK
posted Hide Post
quote:
just tossing a new $20 capacitor on the outside unit would be a reasonable first troubleshooting step based in this case.


Provided you understand the risks and procedure for discharging the old capacitor. Watching the videos on utoob are good, you'll learn what to do, and watch plenty to get it down.
 
Posts: 24165 | Location: Florida | Registered: November 07, 2008Reply With QuoteReport This Post
Fighting the good fight
Picture of RogueJSK
posted Hide Post
Yeah, the video I posted above goes through how to safely discharge the capacitor, before it ever gets into how to test it.

And the OP stated that he's already replaced the capacitors before. So hopefully he knew how to safely do that already...
 
Posts: 32992 | Location: Northwest Arkansas | Registered: January 06, 2008Reply With QuoteReport This Post
Savor the limelight
posted Hide Post
Clogged condensate line followed by bad run caps are by far the most common reasons our ACs stop running.
 
Posts: 11544 | Location: SWFL | Registered: October 10, 2007Reply With QuoteReport This Post
Member
Picture of konata88
posted Hide Post
Thanks guys.

I've replaced it once in all my years - I was gonna ask again how to safely discharge. Smile I'll watch the video.

I think I found a cap locally in stock. Will test and then go buy one. If test indicates the cap is still working, I'll come back here first.




"Wrong does not cease to be wrong because the majority share in it." L.Tolstoy
"A government is just a body of people, usually, notably, ungoverned." Shepherd Book
 
Posts: 13069 | Location: In the gilded cage | Registered: December 09, 2007Reply With QuoteReport This Post
Age Quod Agis
Picture of ArtieS
posted Hide Post
Usually a clogged condensate line cuts power to the thermostat, which then reads a power error. It's worth a look, but I still think that since the compressor is making noises like it is trying to start, it is getting signal from the thermostat, and the problem is in the capacitors.

Both are possible, though. Our AC failed last week for a clogged condensate line, and it just took a quick shop vac effort to clear it.



"I vowed to myself to fight against evil more completely and more wholeheartedly than I ever did before. . . . That’s the only way to pay back part of that vast debt, to live up to and try to fulfill that tremendous obligation."

Alfred Hornik, Sunday, December 2, 1945 to his family, on his continuing duty to others for surviving WW II.
 
Posts: 12910 | Location: Central Florida | Registered: November 02, 2008Reply With QuoteReport This Post
Ammoholic
Picture of Skins2881
posted Hide Post
quote:
I was gonna ask again how to safely discharge.


Use a screwdriver to short the terminals on the cap.



Jesse

Sic Semper Tyrannis
 
Posts: 21094 | Location: Loudoun County, Virginia | Registered: December 27, 2014Reply With QuoteReport This Post
אַרְיֵה
Picture of V-Tail
posted Hide Post
quote:
Originally posted by ArtieS:
Usually a clogged condensate line cuts power to the thermostat
Yeah, if my line clogs and the drain water backs up, the float switch kills power to the thermostat and the thermostat's LCD display goes blank.



הרחפת שלי מלאה בצלופחים
 
Posts: 31341 | Location: Central Florida, Orlando area | Registered: January 03, 2010Reply With QuoteReport This Post
Member
Picture of Greymann
posted Hide Post
My daughters AC went down last week. Symptoms similar. I replaced capacitor, no luck. The problem was a bad condenser fan, I bought an aftermarket one so far so good.
Oem fan>>>585.00
Aftermarket >>>285.00

Test your fan.
 
Posts: 1645 | Location: New Mexico | Registered: March 21, 2017Reply With QuoteReport This Post
Member
Picture of konata88
posted Hide Post
Thanks guys!! I appreciate the quick and specific help.

Looks like it was the cap at the condenser. I replaced it and cool air is being delivered!!

And I didn't kill myself - was still very apprehensive and tried to short the cap 5 times with a very long screwdriver.

The cap measured 1nF on the Fluke. Both Herm and Fan.

Dumb question: If they didn't have my size in stock (35+5), can I use a different size, at least temporarily? Or is that very bad? Not sure which way would be okay - 40+5? 30+5? How much different would be okay if the one I need is not in stock?

I got lucky this time and bought the last one.




"Wrong does not cease to be wrong because the majority share in it." L.Tolstoy
"A government is just a body of people, usually, notably, ungoverned." Shepherd Book
 
Posts: 13069 | Location: In the gilded cage | Registered: December 09, 2007Reply With QuoteReport This Post
Member
posted Hide Post
Is it too late to suggest calling the man ?





Safety, Situational Awareness and proficiency.



Neck Ties, Hats and ammo brass, Never ,ever touch'em w/o asking first
 
Posts: 55141 | Location: Henry County , Il | Registered: February 10, 2004Reply With QuoteReport This Post
Alienator
Picture of SIG4EVA
posted Hide Post
Capacitor is the easiest to trouble shoot and a common failure.


SIG556 Classic
P220 Carry SAS Gen 2 SAO
SP2022 9mm German Triple Serial
P938 SAS
P365 FDE

Psalm 118:24 "This is the day which the Lord hath made; we will rejoice and be glad in it"
 
Posts: 7136 | Location: NC | Registered: March 16, 2012Reply With QuoteReport This Post
Member
Picture of Greymann
posted Hide Post
quote:

Dumb question: If they didn't have my size in stock (35+5), can I use a different size, at least temporarily?


************************

I believe you can only deviate 10%.
The first number is for your compressor, you don't want to ruin that.

Call your local hvac supply house, they will have it or get the right one.
But if the supply house is like the ones here they won't sell it to you. But ask who will sell to you.

I had to have a plumbing company get my parts then I buy from them.

Last year I bought a spare from Amazon, but it was a bait and switch.
I received a generic chicom cap. and it was a smaller diameter than original one so wouldn't fit in the bracket.
Sent it back.

I don't know why most hvac wholesale supplier only sell to repair shops.

.
 
Posts: 1645 | Location: New Mexico | Registered: March 21, 2017Reply With QuoteReport This Post
Dances With
Tornados
posted Hide Post
Glad you got yours fixed.

Just a FYI: Around here there has been a rash of the outside unit not coming on and the Start Capacitor is actually fine, not needing replacement.

This is just a FYI but it's interesting and something one can ask the AC repair guy about.

It's just a weird year, it happens, but honest repairmen have found the contacts in the outside unit packed with spiders and ants and little tiny insects that prevent the contacts from closing all the way properly.

A little bit of cleaning out the infestation and the contacts and all is good for most people.

In some cases an honest AC repair guy has had to actually replace the contacts, but that is very cheap and easy to do.

BEWARE BEWARE BEWARE, don't even thinking about looking inside the unit until THE POWER IS PULLED AND OFF !!!!! This is high voltage!

Electricity and a limp schlong, what do they have in common? One does NOT f*** with either.
.
 
Posts: 11964 | Registered: October 26, 2009Reply With QuoteReport This Post