Code question for electricians Login/Join 
Three Generations
of Service
Picture of PHPaul
posted
Are the stab connectors for splicing wire rated for stranded wire?

Daughter complained of kitchen light flickering. Dual bulb flush mount fixture.
Pulled it down the stranded neutral from one of the sockets was pulled out (I assume it was loose in the connector before I removed the fixture) and there were two sets of connectors: One set tying the two socket leads to a pigtail, another tying the pigtail to the Romex.

Also, the stranded ground on the fixture was just wrapped around the solid ground on the Romex. No wirenut or tape or anything at all.

Wound up shitcanning the fixture and putting a new one in.




Be careful when following the masses. Sometimes the M is silent.
 
Posts: 15659 | Location: Downeast Maine | Registered: March 10, 2010Reply With QuoteReport This Post
Ammoholic
Picture of Skins2881
posted Hide Post
Wouldn't know, I refuse to used them. Usually if they are used on stranded wiring then the wires are tinned.

The ground wire should have a wire nut installed.



Jesse

Sic Semper Tyrannis
 
Posts: 21358 | Location: Loudoun County, Virginia | Registered: December 27, 2014Reply With QuoteReport This Post
Member
posted Hide Post
While it works, I do not believe stranded is intended for residential permanent wiring applications. I would not use it in the push in type connections I think you are describing. Some fixtures have a choice, push in or around a screw. I have always preferred the screw for exactly this reason - stab in type gives a poor connection.
 
Posts: 2168 | Location: south central Pennsylvania | Registered: November 05, 2008Reply With QuoteReport This Post
Delusions of Adequacy
Picture of zoom6zoom
posted Hide Post
The guy who invented stab in connectors should be... stabbed.




I have my own style of humor. I call it Snarkasm.
 
Posts: 17944 | Location: Virginia | Registered: June 02, 2006Reply With QuoteReport This Post
Security Sage
Picture of striker1
posted Hide Post
Stab connectors should be done away with. Same for the back-stabs on receptacles.



RB

Cancer fighter (Non-Hodgkins Lymphoma) since 2009, now fighting Diffuse Large B-Cell Lymphoma.


 
Posts: 7133 | Location: Michiana | Registered: March 01, 2005Reply With QuoteReport This Post
Ammoholic
Picture of Skins2881
posted Hide Post
quote:
Originally posted by striker1:
Stab connectors should be done away with. Same for the back-stabs on receptacles.


Hey now, careful what you say, those things pay my mortgage. If we eliminated those we'd have way fewer electrical failures and I might have to seek a second job.



Jesse

Sic Semper Tyrannis
 
Posts: 21358 | Location: Loudoun County, Virginia | Registered: December 27, 2014Reply With QuoteReport This Post
Member
posted Hide Post
quote:
Originally posted by Chris42:
While it works, I do not believe stranded is intended for residential permanent wiring applications. I would not use it in the push in type connections I think you are describing. Some fixtures have a choice, push in or around a screw. I have always preferred the screw for exactly this reason - stab in type gives a poor connection.


On yachts, they only use stranded wire. Usually tinned unless it's a budget builder. But, the Euro yachts all use those poke and stab terminal blocks for all of the wiring, it holds the stranded wire without issue, I hate the poke and stab crap.
 
Posts: 21429 | Registered: June 12, 2005Reply With QuoteReport This Post
Member
posted Hide Post
quote:
Originally posted by PHPaul:
Are the stab connectors for splicing wire rated for stranded wire?


No, and I wouldn't use them on solid wire either.




 
Posts: 10062 | Registered: October 15, 2008Reply With QuoteReport This Post
Ammoholic
Picture of Skins2881
posted Hide Post
quote:
Originally posted by Excam_Man:
quote:
Originally posted by PHPaul:
Are the stab connectors for splicing wire rated for stranded wire?


No, and I wouldn't use them on solid wire either.


Actually for some odd reason they are.




Jesse

Sic Semper Tyrannis
 
Posts: 21358 | Location: Loudoun County, Virginia | Registered: December 27, 2014Reply With QuoteReport This Post
Three Generations
of Service
Picture of PHPaul
posted Hide Post
I'll be damned. Down to #18 too.

Not in my house, Bubba!




Be careful when following the masses. Sometimes the M is silent.
 
Posts: 15659 | Location: Downeast Maine | Registered: March 10, 2010Reply With QuoteReport This Post
  Powered by Social Strata  
 