Running a Natural Gas line for a Dryer??? Login/Join 
Member
Picture of SOTAR
posted
My home currently has natural gas service. (Stove, Furnance, Water heater.) However, the dryer is electric and I do not have a gas line that runs to the laundry room.

Purchased a (new to me) 1-year-old dryer and was able to buy it for 1/3 the cost of a new unit. My prior dryer is 20 years old and I've done any/all the repairs on it myself over that time.

So I need a gas line installed from the garage to the laundry room. about 25' horizontal and up to the 2nd floor, maybe 12-14' verticle.



Options:

1) I could run the pipe or hose myself. The total run would be around 30 feet. Across a crawlspace and up to the 2nd floor where the laundry room is. Then get a contractor to connect the new pipe to the existing source and add a valve in the laundry room. (I'm handy enough to do it myself, just figure that I could do the grunt work and save money. Let the contractor do the connections)

2) just contract it out.


The problem: I'm not a natural gas supply expert.

- I don't know if I need to use a steel pipe, copper tubing, or some sort of modern plastic hose. I can cut and thread pipe, get the correct goop for the treads and do that.

- The stove is vertically in line with where the dryer is at. So in theory a line could be run down through the wall to the crawlspace and then insert a T splice to connect there. Or if that isn't acceptable run it 20-30 feet over to the garage where the feed to the furnace and water heater is located.


I know the simple but more expensive answer is to have a contractor do it. Unfortunately, I'm not making bank any longer as I'm training for a new career. Thus trying to find the best way to be safe but save money.


__________________________
My door is always open to Sigforum members, and I'm always willing to help if I can.
 
Posts: 1040 | Location: portland, OR | Registered: October 29, 2008Reply With QuoteReport This Post
Get my pies
outta the oven!

Picture of PASig
posted Hide Post
You need to let an expert do this.

NG is nothing to eff around with if you don’t know what you’re doing.

Get a good plumber, they can run what’s called CSST which is a flex stainless steel tube that’s covered in a black rubber jacket. When I got natural gas installed in my house in 2017, the HVAC guy ran what’s called TracPipe CounterStrike CSST to my heater and water heater.


 
Posts: 35384 | Location: Pennsylvania | Registered: November 12, 2007Reply With QuoteReport This Post
Member
posted Hide Post
Call the man, lic. Bonded, insured.





Safety, Situational Awareness and proficiency.



Neck Ties, Hats and ammo brass, Never ,ever touch'em w/o asking first
 
Posts: 55400 | Location: Henry County , Il | Registered: February 10, 2004Reply With QuoteReport This Post
Shall Not Be Infringed
Picture of nhracecraft
posted Hide Post
quote:
Originally posted by PASig:
You need to let an expert do this.

NG is nothing to eff around with if you don’t know what you’re doing.

Get a good plumber, they can run what’s called CSST which is a flex stainless steel tube that’s covered in a black rubber jacket. When I got natural gas installed in my house in 2017, the HVAC guy ran what’s called TracPipe CounterStrike CSST to my heater and water heater.

More often CSST has a Yellow jacket...Just sayin' Wink


____________________________________________________________

If Some is Good, and More is Better.....then Too Much, is Just Enough !!
Trump 47....Make America Great Again!
"May Almighty God bless the United States of America" - parabellum 7/26/20
Live Free or Die!
 
Posts: 9794 | Location: New Hampshire | Registered: October 29, 2011Reply With QuoteReport This Post
Member
posted Hide Post
The natural gas supplier where I live have employees who do work like this. Contact them and see if they do it or can recommend a contractor.


_________________________
"Sometimes I wonder whether the world is being run by smart people who are putting us on or by imbeciles who really mean it."
Mark Twain
 
Posts: 13553 | Registered: January 17, 2011Reply With QuoteReport This Post
A Grateful American
Picture of sigmonkey
posted Hide Post
The meter has to be rated for the total useable BTU of all sources. If it falls too low, you can have serious issues with efficiency or function of appliances, incorrect burning (gas/air ratio), loss of flame and resulting gas leak/build up.

As stated. "Call the man."




"the meaning of life, is to give life meaning" Ani Yehudi אני יהודי Le'olam lo shuv לעולם לא שוב!
 
Posts: 44871 | Location: Box 1663 Santa Fe, New Mexico | Registered: December 20, 2008Reply With QuoteReport This Post
semi-reformed sailor
Picture of MikeinNC
posted Hide Post
My dads a plumber, he runs his own stuff for propane and NG. When he ran a line in my kids house, dad was telling me about how the meter is gauged for the amount of all the items using gas at the same time. Someone else said that above in the comments.

Unless you’re a plumber….Call the man. Pay the money and then you won’t have to worry about killing yourself or your family.



"Violence, naked force, has settled more issues in history than has any other factor.” Robert A. Heinlein

“You may beat me, but you will never win.” sigmonkey-2020

“A single round of buckshot to the torso almost always results in an immediate change of behavior.” Chris Baker
 
Posts: 11621 | Location: Temple, Texas! | Registered: October 07, 2006Reply With QuoteReport This Post
drop and give me
20 pushups
posted Hide Post
Donot do yourself.... Call the man.... check for local permits..... Check with homeowners insurance carrier if allowed another gas applaince added without their knowledge because if something bad should happen and things go wrong they might void your coverage............................ Just my 2cts. .... drill sgt.
 
Posts: 2199 | Location: denham springs , la | Registered: October 19, 2019Reply With QuoteReport This Post
Savor the limelight
posted Hide Post
There was an attorney who used post here P239 something or another. He once asked about using epoxy to fix a leaking gas pipe he had. I think my advice to him was doing gas lines yourself is like when a regular person represents themselves in court instead of hiring an attorney. You can do it yourself, but you’ll lose out on the knowledge, experience, and peace of mind that hiring a pro can provide.
 
Posts: 12251 | Location: SWFL | Registered: October 10, 2007Reply With QuoteReport This Post
Member
Picture of 4MUL8R
posted Hide Post
Your home, when sold, also needs to provide safe occupancy for the new owner. Not having a licensed installation is problematic.

The savings on the dryer are now likely eliminated by the cost for the gas line. However, the drying process would be improved.


-------
Trying to simplify my life...
 
Posts: 5344 | Location: Commonwealth of Virginia | Registered: January 15, 2007Reply With QuoteReport This Post
paradox in a box
Picture of frayedends
posted Hide Post
In addition to meter supply, there can be an issue if you are tapping into existing line that isn’t big enough to supply everything.




These go to eleven.
 
Posts: 12605 | Location: Westminster, MA | Registered: November 14, 2006Reply With QuoteReport This Post
Don't Panic
Picture of joel9507
posted Hide Post
Don't save a buck, call your gas utility company and ask them to have someone run the line.

Get it done by the book, by someone who knows the book.

DIY natural gas is a newspaper headline in the making.
 
Posts: 15255 | Location: North Carolina | Registered: October 15, 2007Reply With QuoteReport This Post
Member
Picture of sigcrazy7
posted Hide Post
I ran a new line myself about twenty years ago. I did it in black steel pipe. Honestly, by the time you bought the pipe threader, pipe vice, and other tools, you’re money ahead to just have someone run CSST.



Demand not that events should happen as you wish; but wish them to happen as they do happen, and you will go on well. -Epictetus
 
Posts: 8292 | Location: Utah | Registered: December 18, 2008Reply With QuoteReport This Post
Member
Picture of SOTAR
posted Hide Post
Thank you, everyone.

Decision made, contractor to do the work.

trapper189
quote:
There was an attorney who used post here P239 something or another.
After reading your reply, I believe I remember you posting that prior.


__________________________
My door is always open to Sigforum members, and I'm always willing to help if I can.
 
Posts: 1040 | Location: portland, OR | Registered: October 29, 2008Reply With QuoteReport This Post
Ammoholic
posted Hide Post
quote:
Originally posted by SOTAR:
Decision made, contractor to do the work.

Wise decision. Good luck, hope you find an excellent and timely contractor.
 
Posts: 7274 | Location: Lost, but making time. | Registered: February 23, 2011Reply With QuoteReport This Post
Thank you
Very little
Picture of HRK
posted Hide Post
quote:
Originally posted by SOTAR:
Decision made, contractor to do the work.


Excellent choice

 
Posts: 24844 | Location: Gunshine State | Registered: November 07, 2008Reply With QuoteReport This Post
Member
posted Hide Post
In this case, I'd suggest letting the pro do it, just because he might balk at being responsible for the whole system while only installing the valve. Might be more hassle than cost.

That said, I ran 24' of CSST in my shop - it wasn't that hard, except I got a bad o-ring out the box. More likely, someone else nicked it & traded one out. I had the guys that installed my boiler look at it before I closed the walls up & they said it looked fine.
 
Posts: 3360 | Location: IN | Registered: January 12, 2007Reply With QuoteReport This Post
would not care
to elaborate
Picture of sse
posted Hide Post
Me and a buddy did it, mostly him. I did some calculations on consumption when running the range, furnace, etc., to make sure there wasn't a capacity issue. We have an old school hardware store nearby, they cut the pipes to specs, tapped all the fittings.

I did learn one thing I wasn't aware of. You know how they always say put soapy water on the fittings to check for leaks? Well, it turns out that is not simply to find minute leaks with a magnifying glass at fittings you didn't quite snug up enough. It's to find major leaks on loose fittings you neglected to tighten...at all. Quit one evening and next morning all was together, but found one of those. My bud was more knowledgeable than careful.
 
Posts: 3076 | Location: USA | Registered: June 12, 2008Reply With QuoteReport This Post
Team Apathy
posted Hide Post
My brother and I ran a new gas line, upgrading a half inch to a full
inch, in order to support a tankless water heater. It wasn’t hard, though my physical situation was very simple and straight forward… only surface level runs in the garage.

This was several years ago with no issues.
 
Posts: 6569 | Location: Modesto, CA | Registered: January 27, 2005Reply With QuoteReport This Post
Member
posted Hide Post
I've done black pipe and CSST. After using CSST I'll never use black pipe again except where required by code. Take the little online course for CSST install (this stuff is pretty much fool proof compared to black pipe) - pull the permit - get the inspection (leak down test here) and done.

edited to add I've also had my meter moved and completely redid the gas plumbing in the house at that time.




I reject your reality and substitute my own.
--Adam Savage, MythBusters
 
Posts: 1785 | Location: Red Wing, MN | Registered: January 04, 2005Reply With QuoteReport This Post