We have 2 garage openers. Couple of weeks ago, it rained for couple of days here in Las Vegas. Wife called me to let me nnow garage opener #1 will not open. When I got home, circuit breaker was tripped. I turned it OFF, then switched it back ON. Back to normal operation.

It was raining again since last night. Garage opener #2 is DEAD. Opener #1 is OK. I realized they are on separate breakers. I reset the main switch breaker and pushed
It back to ON. Went back inside the garage to reset the outlet with GCFI. Did it twice.
On both instances, the MAIN circuit breaker controlling #2 will trip again. It is telling
Me something is grounded somewhere. Any idea or previous similar issues?

I will wait until it stop raining and try it again.
Not sure if this is a service call for an electrician.

Thoughts?


_______________________
P228 - West German
 
Posts: 1886 | Location: Las Vegas | Registered: November 05, 2003Reply With QuoteReport This Post
Member
posted Hide Post
It sounds like somewhere you have a connection that is getting wet. What is over the garage ceiling? Roof? Attic? You may have a roof leak which is leaking onto the junction box the garage door is plugged into or something along those lines. Usually garage wiring and outlets are a good distance above the floor, so rain or water dripping off of cars shouldn't effect it.
 
Posts: 21335 | Registered: June 12, 2005Reply With QuoteReport This Post
Save today, so you can
buy tomorrow
posted Hide Post
jimmy, our living room and one bedroom is above our garage. Garage opener outlets are all dry.

I also noticed that the light inside the home number address box is OUT. But I noticed that when opener #1 went OUT few weeks ago.


_______________________
P228 - West German
 
Posts: 1886 | Location: Las Vegas | Registered: November 05, 2003Reply With QuoteReport This Post
Member
Picture of PowerSurge
posted Hide Post
Yes, you’ve got a connection that is getting wet. It is more than likely an outside receptacle that is on that GFCI circuit. Seen it many times. The waterproof gasket(s) are probably bad or installed incorrectly and need to be replaced.


———————————————
The fool hath said in his heart, There is no God. Psalm 14:1
 
Posts: 3969 | Location: Northeast Georgia | Registered: November 18, 2017Reply With QuoteReport This Post
Save today, so you can
buy tomorrow
posted Hide Post
Powersurge, thanks for the tip. I have an outside outlet that I use for my RV. I will check on that when the rain stop. Will also check any other outside outlets.


_______________________
P228 - West German
 
Posts: 1886 | Location: Las Vegas | Registered: November 05, 2003Reply With QuoteReport This Post
Member
Picture of az4783054
posted Hide Post
It could be as simple as the water resistant cover didn't get closed after last use. It's happened before.


Beware of a man whose only pistol is a 1911, he's probably very good with it.
 
Posts: 11194 | Location: Somewhere north of a hot humid hell in the summer. | Registered: January 09, 2009Reply With QuoteReport This Post
My other Sig
is a Steyr.
Picture of .38supersig
posted Hide Post
If you have a QO breaker, they will trip and go bad in an environment of high humidity.




 
Posts: 9155 | Location: Somewhere looking for ammo that nobody has at a place I haven't been to for a pistol I couldn't live without... | Registered: December 02, 2014Reply With QuoteReport This Post
Save today, so you can
buy tomorrow
posted Hide Post
I just looked around the garage to see if anything else is NOT working right now. I noticed that the landscape controller pannel is also OFF. I remember seeing a box burried on the ground that have a green cover. When I opened it before, I saw bunch of wires that I think controls the water sprinkler. Are those wires water proof? I remember seeing some water inside that box before, but not deep enough at that time to submerge those wires. Im wondering if that could be the one causing the problem.


_______________________
P228 - West German
 
Posts: 1886 | Location: Las Vegas | Registered: November 05, 2003Reply With QuoteReport This Post
Ammoholic
Picture of Skins2881
posted Hide Post
Are the breakers actually tripping? If they are are they GFI breakers? You said main breaker is tripping, but from your description it sounds like you are actually talking about branch circuit breakers.

What year was the house built?



Jesse

Sic Semper Tyrannis
 
Posts: 20824 | Location: Loudoun County, Virginia | Registered: December 27, 2014Reply With QuoteReport This Post
Ammoholic
Picture of Skins2881
posted Hide Post
Sprinkler system likely won't trip stuff, it's controlled by low voltage wiring.



Jesse

Sic Semper Tyrannis
 
Posts: 20824 | Location: Loudoun County, Virginia | Registered: December 27, 2014Reply With QuoteReport This Post
Save today, so you can
buy tomorrow
posted Hide Post
Skins, the main electric circuit breaker inside those huge grey boxes trips. When I reset the switch in the pannel, the garage opener is still DEAD. After resetting the switch, I noticed one electeical outlet inside the garage with the GCFI light ON and need to be reset as well. When I pressed the reset button, it tripped the main pannel again. I did this twice. It seems like that outlet is also connected to the garage opener.

House was built 2015.


_______________________
P228 - West German
 
Posts: 1886 | Location: Las Vegas | Registered: November 05, 2003Reply With QuoteReport This Post
Ammoholic
Picture of Skins2881
posted Hide Post
I'm pretty sure you are not talking about the bmain, just a regular individual breaker. The rest of the house stays on right?

What you are discribing sounds like a dead short.
Does it immediately trip? Is there a small spark visible when it does?

The garage GFI, given your year of construction should cover exterior outlets, garage, and possibly basement unfinished basement outlet.

Do you have a post light or any landscape lighting?



Jesse

Sic Semper Tyrannis
 
Posts: 20824 | Location: Loudoun County, Virginia | Registered: December 27, 2014Reply With QuoteReport This Post
Save today, so you can
buy tomorrow
posted Hide Post
Skins, thank you for taking the time to respond. You are correct. It is an individual circuit breaker that trips. The rest of the house have power.

The first time I pressed the outlet GCFI reset button, I DID saw a spark. The second time I tried it, it did not have any spark.

I do have a low voltage path light that I
Installed myself. The transformer is plugged into the outside
Outlet. And it is working and do have power right now.


_______________________
P228 - West German
 
Posts: 1886 | Location: Las Vegas | Registered: November 05, 2003Reply With QuoteReport This Post
Ammoholic
Picture of Skins2881
posted Hide Post
What about any post light in your yard or pier lights at end of driveway?

I have a bunch of process of elimination type of questions to ask you, it'd be a pain in the but to do on here, if you email me your number I can walk you through what to check. If you are not a mechanically inclined person or don't feel comfortable with handling electrical equipment, then you need an electrician. He will need to isolate where in the circuit the fault is a correct or rewire the issue is.

This message has been edited. Last edited by: Skins2881,



Jesse

Sic Semper Tyrannis
 
Posts: 20824 | Location: Loudoun County, Virginia | Registered: December 27, 2014Reply With QuoteReport This Post
Member
posted Hide Post
Your sprinkler system manifold should only be 24v and would not short a house circuit. If it did short, you may loose that zone on your panel.

The feed to your control panel must be on the same circuit that popped. I would check all outside outlet covers, and gaskets first, as mention before.

I chased the same issue when I bought my first house. Fixed all of the exterior outlets and still had the same problem. After months of investigating, I found that my dormer bathroom roof valley was leaking. It was dripping down inside the wall to my garage, exactly where a gfi was installed. I had the roof done a few months later (it was due anyway) and swapped out the gfi for good measures. Problem finally resolved.

Good luck and keep at it.

-Jeff
 
Posts: 170 | Location: NJ | Registered: September 06, 2015Reply With QuoteReport This Post
Member
posted Hide Post
The GFCI outlet itself can also go bad and require replacement, although not usually in just 4 years.
 
Posts: 1179 | Location: NE Indiana  | Registered: January 20, 2011Reply With QuoteReport This Post
Save today, so you can
buy tomorrow
posted Hide Post
OK. I just finished replacing the GFCI outlet in the garage. Used my tester for LINE (124 V). LOAD Line is ZERO. I turned OFF the 20Amp circuit breaker from outside pannel. Replaced the GFCI. Turned back ON the 20Amp circuit breaker. LINE showed 124V. LOAD Line showed ZERO. I pressed the RESET button. It Trips the circuit breaker AGAIN. That tells me it is NOT faulty GFCI.

Any other thoughts? Or should I call an electrician now?


_______________________
P228 - West German
 
Posts: 1886 | Location: Las Vegas | Registered: November 05, 2003Reply With QuoteReport This Post
The Unmanned Writer
Picture of LS1 GTO
posted Hide Post
Ador- have you replaced both circuit breakers?

Best thing I found was a great household electrician.

With myself being a highly experienced aircraft electrician, I am able to see his quality and, he and I, are able to speak on the same level.






Life moves pretty fast. If you don't stop and look around once in a while, you could miss it.



"If dogs don't go to Heaven, I want to go where they go" Will Rogers

The definition of the words we used, carry a meaning of their own...



 
Posts: 14038 | Location: It was Lat: 33.xxxx Lon: 44.xxxx now it's CA :( | Registered: March 22, 2008Reply With QuoteReport This Post
Yokel
Picture of ontmark
posted Hide Post
Ok I am not an electrician.

Just a thought.

He said he has installed a new GFCI Outlet to replace the one that was there.

Reset the line main breaker.

When he pushes the reset button on the new GFCI outlet it trips the line main breaker again.

Could it be something wire downstream on the same feed that is shorted?

It loses voltage when the upstream GFCI outlet is tripped. Thus allowing the Line main breaker to be reset. Then when the reset on the GFCI Outlet is reset, the downstream feed come on, and the downstream problem trips main line breaker.



Beware the man who only has one gun. He probably knows how to use it! - John Steinbeck
 
Posts: 3878 | Location: Vallejo, CA | Registered: August 18, 2007Reply With QuoteReport This Post
Ammoholic
posted Hide Post
quote:
Originally posted by ontmark:
Ok I am not an electrician.

Just a thought.

He said he has installed a new GFCI Outlet to replace the one that was there.

Reset the line main breaker.

When he pushes the reset button on the new GFCI outlet it trips the line main breaker again.

Could it be something wire downstream on the same feed that is shorted?

It loses voltage when the upstream GFCI outlet is tripped. Thus allowing the Line main breaker to be reset. Then when the reset on the GFCI Outlet is reset, the downstream feed come on, and the downstream problem trips main line breaker.

Yes, that is exactly what is going on. Unfortunately, unless one installed the wiring (and has a functional memory Smile), one often does not know what route the circuit takes or even what all the loads on it are. Hence Jessie’s process of elimination questions...
 
Posts: 6919 | Location: Lost, but making time. | Registered: February 23, 2011Reply With QuoteReport This Post