It finally got hot enough around here to turn on the A/C unit. I was happy when it fired right up and cooled down the house. When I woke up the next day,It was no longer blowing anything out of the registers.
The A/C unit is a Rheem 2.5 ton, the furnace is a Amana forced air. I have NG heat. The A/C unit is about 6years old.
I'm leaning towards the thermostat as the problem. I get nothing out of any control setting, no A/C, no heat,no fan only.
The thermostat has two AAA batteries, I replaced both, no change.

Is there another part of the controls for the HVAC system besides the thermostat that controls the various systems?
 
Posts: 5247 | Location: Chicago, IL, USA: | Registered: November 17, 2002Reply With QuoteReport This Post
"The deals you miss don’t hurt you”-B.D. Raney Sr.
posted Hide Post
I didn’t see anything in your post about checking breakers.
Could be tripped out.
 
Posts: 6498 | Location: East Texas | Registered: February 20, 2008Reply With QuoteReport This Post
Drill Here, Drill Now
Picture of tatortodd
posted Hide Post
I have heat pumps so the Outdoor condensor is needed whether heating or cooling. #1 failure in my neck of the woods is the capacitor on the outdoor condensor.

Go outdoors to the AC condensor and see if it's making a noise like it's trying to start a fan, but the fan isn't starting.

If it's that, you need a new capacitor. Chinese ones are $20ish and made in the USA are $30ish (e.g. AMRAD sold on Amazon). They come in different sizes, but this is the one for mine.

I always keep it and/or a universal capacitor on my garage shelf so I don't get desparate and shell out big $$ locally during Houston's miserable summer.



Ego is the anesthesia that deadens the pain of stupidity

DISCLAIMER: These are the author's own personal views and do not represent the views of the author's employer.
 
Posts: 25499 | Location: Northern Suburbs of Houston | Registered: November 14, 2005Reply With QuoteReport This Post
Truth Seeker
Picture of StorminNormin
posted Hide Post
I am BEYOND NOT AN AC tech, but saying even the fan only won’t run makes me think it does have something to do with the thermostat. I don’t know if you have an analog or digital thermostat. I once had a problem where the thermostat kept turning off and it turned out the condensation was not draining so it triggered a switch that shut off the thermostat so it would not keep running. Once I blew out the drain line with compressed air, all was good.

Other thing is as Tator said, which could be the capacitor.




NRA Benefactor Life Member
 
Posts: 9861 | Location: The Lone Star State | Registered: July 07, 2008Reply With QuoteReport This Post
Member
Picture of SIGfourme
posted Hide Post
Check the drip pan to see if it’s full of water. May have a plugged trap.
 
Posts: 2482 | Location: Southeast CT | Registered: January 18, 2009Reply With QuoteReport This Post
Member
Picture of wrightd
posted Hide Post
https://scontent-den2-1.xx.fbc...4OrEkbIQ&oe=6A12E5D7




Lover of the US Constitution
Wile E. Coyote School of DIY Disaster
 
Posts: 9952 | Location: Nowhere the constitution is not honored | Registered: February 01, 2008Reply With QuoteReport This Post
A Grateful American
Picture of sigmonkey
posted Hide Post
Thermostat calls for cooling, the 24v transformer sends current on the Y and R wires to the contactor (relay) and closes it permitting 240V to both the fan and the compressor, and the capacitor(s) are tied to the fan and compressor.

(some systems have one capacitor for the fan, and one for the compressor, and some have one that is a dual capacitor that handles both the fan and the compressor)

The air handler fan (in the inside unit) is controlled by the thermostat when the system calls for cooling and closes the relay on the circuit board in the air handler and supplies the 120v to the fan motor)

At the condenser, you should hear the contactor energizing as it makes a pretty loud click, similar to a car starter solenoid.

You can check the transformer to see if it is supplying 24v
use a multimeter set on AC and probe the Common and Hot terminals (marked C and R), if you have 24-28V the transformer is good.

If you don't have power, look for a small glass style fuse on the control board in the air handler and see if it has blown.

If it's good, check the primary (120v) side of the transformer (two 120v 14 awg wires) these will be controlled by the 20A breaker in the home fuse panel.


If all that checks good, open the breaker to the air handler and connect the Red Yellow Green (jumpers or wirenut) then turn the breaker on, and if the condenser unit fan/compressor come on, and the air handler fan comes on and you get cooling air, replace the thermostat.

If you have questions, post back.

The condenser has 24v and 240v, so just mess with the inside first.

And it is not uncommon (especially first start up of the AC season) for more than one thing to go wrong sequentially (cascading/symathetic failure) with contactors, capacitors and thermostats.




"the meaning of life, is to give life meaning" Ani Yehudi אני יהודי Le'olam lo shuv לעולם לא עוד
 
Posts: 46415 | Location: Box 1663 Santa Fe, New Mexico | Registered: December 20, 2008Reply With QuoteReport This Post
Partial dichotomy
posted Hide Post
quote:
Originally posted by SIGfourme:
Check the drip pan to see if it’s full of water. May have a plugged trap.


Good easy first check. Especially since it hasn't been running. Dried crap in the drain maybe. Then the capacitor on the condensing unit.




SIGforum: For all your needs!
Imagine our influence if every gun owner in America was an NRA member! Click the box>>>
 
Posts: 41730 | Location: SC Lowcountry/Cape Cod | Registered: November 22, 2002Reply With QuoteReport This Post
Savor the limelight
posted Hide Post
quote:
Originally posted by SIGfourme:
Check the drip pan to see if it’s full of water. May have a plugged trap.

This is the first thing to check. At the air handler, you will see wires going into a PVC T on the condensate line. That’s a float switch that shuts everything off of the line gets clogged. Pull the float switch out, stick your finger in the hole to see if it’s full of water. If so, find where outside it drains and suck it out with a wet/dry vac.

There could also be a float switch in the drip pan as well.
 
Posts: 14352 | Location: SWFL | Registered: October 10, 2007Reply With QuoteReport This Post
His Royal Hiney
Picture of Rey HRH
posted Hide Post
I may have a different problem than yours. But two years ago, the A/C stopped working just like yours. I didn't know enough even though I had electronics / electrical training. Called HVAC company, they couldn't come out for a week. We stayed in a hotel cuz it was hot. Turns out, the fuse to the unit blue. It was outside in a box by the unit.



"It did not really matter what we expected from life, but rather what life expected from us. We needed to stop asking about the meaning of life, and instead to think of ourselves as those who were being questioned by life – daily and hourly. Our answer must consist not in talk and meditation, but in right action and in right conduct. Life ultimately means taking the responsibility to find the right answer to its problems and to fulfill the tasks which it constantly sets for each individual." Viktor Frankl, Man's Search for Meaning, 1946.
 
Posts: 21698 | Location: The Free State of Arizona - Ditat Deus | Registered: March 24, 2011Reply With QuoteReport This Post
Member
Picture of 229DAK
posted Hide Post
When mine goes out, it is almost always the filter. The system detects when the filter has reached its end of life and the unit shuts down.


_________________________________________________________________________
“A man’s treatment of a dog is no indication of the man’s nature, but his treatment of a cat is. It is the crucial test. None but the humane treat a cat well.”
-- Mark Twain, 1902
 
Posts: 10381 | Location: Northern Virginia | Registered: November 04, 2005Reply With QuoteReport This Post
Like a party
in your pants
Picture of armored
posted Hide Post
UPDATE:

I checked the breakers in the beginning, no problem. My furnace has a drain for water directly tied to a floor drain, no water pan problems.I had changed the filter about 2 weeks ago.
I checked and found power to the circuit so that was good to go.
I changed the thermostat, problem solved.
 