HVAC question on Goodman/Amana furnace Login/Join 
Member
posted
I have a 15 year old Amana furnace GUCA070BX30 with a PCBBF118S circuit board. The humidifier has stopped working. The 24 volt transformer is not getting any 110 from the circuit board with the furnace and fan running. Does this mean that the circuit board is bad or could there be some other problem?
 
Posts: 1510 | Location: S/W Illinois | Registered: October 29, 2007Reply With QuoteReport This Post
Member
posted Hide Post
Normally, the humidifier terminals are energized with the burners.

You could try the terminals for the electronic air cleaner. They will be energized during a blower call.




 
Posts: 10062 | Registered: October 15, 2008Reply With QuoteReport This Post
Member
posted Hide Post
Wouldn't that activate the humidifier during air conditioning also?
 
Posts: 1510 | Location: S/W Illinois | Registered: October 29, 2007Reply With QuoteReport This Post
Member
posted Hide Post
Yes, but for testing purposes, it would verify operation.

If there's no power on the humidifier terminals, you could wire the low voltage side to the thermostat connections (C and W).




 
Posts: 10062 | Registered: October 15, 2008Reply With QuoteReport This Post