New house we just purchased has a forced-air heating system, the ductwork was installed in 1951 when the home was built and it's built like a Soviet tank. The furnace is a oil-fired Thermo Pride that was installed in 2011. Converting to natural gas is on the list of things to be done but just not happening this year.

The heating works pretty well but we seem to have an issue with one bedroom. Of course it has to be our 6 month old's room and he wakes up crying in the middle of the night because he's cold. I'll walk into the room and it will feel like an instant 10+ degree drop. The register in his room is open but the airflow is very, very weak. My other son's room is on the other side of a wall with this room and when the heat kicks on, you can feel it all the way across the room if I'm sitting with him playing or reading.

Is there a damper somewhere? A blockage? There seems to be no heat making it to this room and the old drafty single pane windows with storm sashes don't help. That's another project when I hit the lottery or rob a bank I jokingly tell my wife.

We had hot water radiator heat at the old house and kept it at 68 morning, day and evening and 65 at night but this system seems too chilly at those temps so I keep it at 70 during the morning, day and evening and 67 overnights.


 
Posts: 33807 | Location: Pennsylvania | Registered: November 12, 2007Reply With QuoteReport This Post
Thank you
Very little
Picture of HRK
posted Hide Post
sounds like their is a blockage of some form, is there a diverter in the path, perhaps the previous owners shut that room down as it wasn't used much, or the duct is clogged.

I would look in the attic to see if there is some kind of manual diverter that directs the air to your other bedroom or to be sure the ducts are unrestricted.

Pull the cover off the duct in the cold room and see if it's blocked there, some folks do that by cutting a small piece of wood to close the end and then put the cover back on like normal.
 
Posts: 23448 | Location: Florida | Registered: November 07, 2008Reply With QuoteReport This Post
Alienator
Picture of SIG4EVA
posted Hide Post
In the interim, get a portable radiator to keep his room warm. My bedroom is just like this, at least 5 degrees cooler than our master bath even though I know air flows. Insulation and ducting is all good.

We keep our house at 68 but have a radiator in my daughters room to keep it at 70.

We have one similar to this.
https://www.homedepot.com/p/De...HygtgCFZN3wQodG8oIAw


SIG556 Classic
P220 Carry SAS Gen 2 SAO
SP2022 9mm German Triple Serial
P938 SAS
P365 FDE

Psalm 118:24 "This is the day which the Lord hath made; we will rejoice and be glad in it"
 
Posts: 7071 | Location: NC | Registered: March 16, 2012Reply With QuoteReport This Post
Ammoholic
Picture of Skins2881
posted Hide Post
quote:
Originally posted by SIG4EVA:
In the interim, get a portable radiator to keep his room warm. My bedroom is just like this, at least 5 degrees cooler than our master bath even though I know air flows. Insulation and ducting is all good.

We keep our house at 68 but have a radiator in my daughters room to keep it at 70.

We have one similar to this.
https://www.homedepot.com/p/De...HygtgCFZN3wQodG8oIAw


Please don't do this.

Space heaters cause 32% of all fires and 79% of heating related fires.

Google results from fire + space heater.



Jesse

Sic Semper Tyrannis
 
Posts: 20821 | Location: Loudoun County, Virginia | Registered: December 27, 2014Reply With QuoteReport This Post
Member
posted Hide Post
Nothing to do with air flow.
Our new edition is over a crawl space. Room got unusually cold, I got under neath & noticed half assed insulation job. I was pissed, took 2 days to finish the job results have been outstanding.

Hope you can the problem for your little man. May he sleep warm & tight.
 
Posts: 5768 | Location: west 'by god' virginia | Registered: May 30, 2009Reply With QuoteReport This Post
Member
Picture of grumpy1
posted Hide Post
I am betting airflow issue based on your description. We had one upstairs bedroom like that. I took the grill off the floor vent and found a damper about 6 inches into the duct from the floor outlet. I opened it fully and all is well. There can also be dampers in other places in the duct work.

You could also try adjusting outlet in the other room that has a lot of air flow to see if that impacts the cold room.
 
Posts: 9747 | Location: Northern Illinois | Registered: March 20, 2009Reply With QuoteReport This Post
Member
posted Hide Post
Ok, so far we have:

Check the attic, and or ductwork for blockage.
Add a portable heater.
Don't add a portable heater.
It is not airflow, add insulation.
It is airflow try monkeying with the dampers.

More information is required in order to make reasonable recommendations. How about some pictures. Also more information on the house and the ductwork would be swell.
 
Posts: 1803 | Location: Spokane, WA | Registered: June 23, 2008Reply With QuoteReport This Post
Just because something is legal to do doesn't mean it is the smart thing to do.
posted Hide Post
Do you have a return register in that room?


Integrity is doing the right thing, even when nobody is looking.
 
Posts: 4134 | Location: Metamora MI | Registered: October 31, 2003Reply With QuoteReport This Post
Paddle your
own canoe
Picture of BigWhup
posted Hide Post
It also could be that there is a hole or tear in the duct going to the cold room. Check the seal where it branches off the main duct as well. a little duct tape may solve the problem.

I am betting on a damper in the attic.
 
Posts: 1553 | Location: South Carolina | Registered: August 06, 2009Reply With QuoteReport This Post
Just because you can,
doesn't mean you should
posted Hide Post
quote:
Originally posted by gjgalligan:
Do you have a return register in that room?


We had a room like that and the lack of a return air duct was the problem.


___________________________
Avoid buying ChiCom/CCP products whenever possible.
 
Posts: 9509 | Location: NE GA | Registered: August 22, 2002Reply With QuoteReport This Post
Ammoholic
Picture of Skins2881
posted Hide Post
Ironically my last call of the day today was a melted outlet. First question out of my mouth, "were you using a space heater?" "Yes."

I told them same thing I posted above about googling the words space heater + fire. Also gave my standard analogy:

Let's say you buy your dream car. A brand new Porsche, fire engine red. Your 80 year old neighbor coincidentally purchases the exact same car the same day. You drive yours to the redline everywhere you go, she drives hers like an 80 year old woman. Which one is more likely to have a catastrophic failure?

Then I explain that's exactly what you're doing when you use a space heater. They draw 1500w, the circuit is 1800w, 80% of entire circuit for one item. That leaves (5) 60w lamps worth of capacity til you reach 100%, after that you should pray your breaker is operating properly.



Jesse

Sic Semper Tyrannis
 
Posts: 20821 | Location: Loudoun County, Virginia | Registered: December 27, 2014Reply With QuoteReport This Post
Muzzle flash
aficionado
Picture of flashguy
posted Hide Post
My old HVAC system was designed with a direct shot from the fan through the coils into one upstairs bedroom and branching ducts to the rest of the house. In winter (heat on) that bedroom was a sauna and in the summer you could hang meat in there. I'd say about 50% of the heating/cooling capacity was directed into that one room. (The air flow into that room was so strong that it actually blew the screws of the outlet cover out when we closed the vents to try to stifle the flow.) I had a diverter installed into the duct to cut off must of the flow so the rest of the house could get some effect.

A couple of years ago a new system was installed and it doesn't have that problem. I'd first check the ducting.

flashguy




Texan by choice, not accident of birth
 
Posts: 27902 | Location: Dallas, TX | Registered: May 08, 2006Reply With QuoteReport This Post
Run Silent
Run Deep

Picture of Patriot
posted Hide Post
Call a Preist...

Someone obviously died in that room and you have a poltergeist.

Sheesh...come on guys...think!

Big Grin


_____________________________
Pledge allegiance or pack your bag!
The problem with Socialism is that eventually you run out of other people's money. - Margaret Thatcher
Spread my work ethic, not my wealth
 
Posts: 6984 | Location: South East, Pa | Registered: July 04, 2002Reply With QuoteReport This Post
Member
Picture of lee40215
posted Hide Post
Is the supply lead in the basement or is the lead in the attic. A lot of basement leads have a damper usually within a foot of the takeoff. Like mentioned before take the register off make sure someone didn’t stuff a towel up inside. If it’s in the attic hard pipe or flex if hard pipe may have to manually feel the pipe and see if there is a damper. If it’s flex verify that the liner hasn’t pulled loose and pulled off or been stepped on a smashed
 
Posts: 1097 | Location: Louisville, Kentucky | Registered: August 28, 2006Reply With QuoteReport This Post
Staring back
from the abyss
Picture of Gustofer
posted Hide Post
quote:
Originally posted by Patriot:
Call a Preist...

Someone obviously died in that room and you have a poltergeist.

Sheesh...come on guys...think!

Big Grin

Beat me to it. That's what I was going with. It's either a ghost or that room is the portal to hell.


________________________________________________________
"Great danger lies in the notion that we can reason with evil." Doug Patton.
 
Posts: 20099 | Location: Montana | Registered: November 01, 2010Reply With QuoteReport This Post
Member
posted Hide Post
Could be several things...

Blocked pipe
Unhooked pipe
Closed damper
Improper ducting
Improper take off location
Lack of return (are you closing the door at night?)
Lack of supply (does it blow warm air at all?)

BTW, radiant heat will always feel warmer than a forced air system.




 
Posts: 10055 | Registered: October 15, 2008Reply With QuoteReport This Post
Nullus Anxietas
Picture of ensigmatic
posted Hide Post
Look for something like this



or this



Somewhere on the duct leading to the under-heated room. The two shown are fully open. At right angles to the duct would be fully-closed.



"America is at that awkward stage. It's too late to work within the system,,,, but too early to shoot the bastards." -- Claire Wolfe
"If we let things terrify us, life will not be worth living." -- Seneca the Younger, Roman Stoic philosopher
 
Posts: 26009 | Location: S.E. Michigan | Registered: January 06, 2008Reply With QuoteReport This Post
Ammoholic
Picture of Skins2881
posted Hide Post
quote:
Originally posted by ensigmatic:
Look for something like this



or this



Somewhere on the duct leading to the under-heated room. The two shown are fully open. At right angles to the duct would be fully-closed.


My dampers are inside the vent with no handles. You need to remove the register reach down into the vent and adjust. Not sure if this is common or not. 1964 construction.



Jesse

Sic Semper Tyrannis
 
Posts: 20821 | Location: Loudoun County, Virginia | Registered: December 27, 2014Reply With QuoteReport This Post
Member
posted Hide Post
After a year of being hot/cold in the new office & just chalking it up to the shitty overall construction, I found that the vent above my desk wasn't hooked in to the HVAC duct. The flex duct was too short, so they just pointed it at the vent - about 4' away. You could feel air moving when the fan was running so......

I found this out when a tree frog landed on my keyboard.
 
Posts: 3297 | Location: IN | Registered: January 12, 2007Reply With QuoteReport This Post
Nullus Anxietas
Picture of ensigmatic
posted Hide Post
quote:
Originally posted by Skins2881:
My dampers are inside the vent with no handles. You need to remove the register reach down into the vent and adjust. Not sure if this is common or not. 1964 construction.

Wow. Why bother? Or do the registers themselves not have controls?

Our home has the levers pictured. It was built in 1967.



"America is at that awkward stage. It's too late to work within the system,,,, but too early to shoot the bastards." -- Claire Wolfe
"If we let things terrify us, life will not be worth living." -- Seneca the Younger, Roman Stoic philosopher
 